    Looking for some guidance here. This 220V beast of an amp has a step up transformer bolted to the bottom of the cab, but only a 2 prong for 120V to get to the primaries.
    Where do I ground the new green wire, is it as simple as running a loooong wire up to the chassis of the amp, as usual?
    Click image for larger version

Name:	IMG_7398.jpg
Views:	211
Size:	2.40 MB
ID:	978105

    Click image for larger version

Name:	IMG_7397.jpg
Views:	191
Size:	3.47 MB
ID:	978104
    Attached Files

  • #2
    here's the plug for the secondaries of the step up to the 220v xformer in the chassis

    Click image for larger version  Name:	IMG_7399.jpg Views:	0 Size:	2.36 MB ID:	978112
    Last edited by LarBal; 02-19-2023, 07:34 PM.

    Comment


    • #3
      Looking dangerous! Click image for larger version

Name:	Screenshot 2023-02-19 at 21.49.57.png
Views:	182
Size:	2.24 MB
ID:	978118

      If you are going to do it, do it properly and use 3 pin connectors with an earthing point.
      Support for Fender, Laney, Marshall, Mesa, VOX and many more. https://jonsnell.co.uk
      If you can't fix it, I probably can.

      Comment


      • #4
        Yea, I was thinking the same, this is how it came to me.

        Comment


        • #5
          Safety grounding must comprise amp chassis as well as the step-up transformer core /brackets.

          Make sure no one can touch the transformer terminals. Electrical tape is not safe enough.
          Install a strain relief for the power cable.

          A self-contained step-up transformer would be a better/safer solution.
          An exposed "PT" without endbells is not safe.
          Last edited by Helmholtz; 02-19-2023, 10:37 PM.