Quote Originally Posted by Helmholtz View Post
Short and simple: For a given core, saturation determines the minimum number of primary turns for max. peak current to be expected.
Not exactly. Core saturation determines the number of turns and core area needed to withstand a certain amount of volt-time integral. That's not directly related to the peak output current to be expected. Primary magnetizing current is not the same as reflected secondary current. The two are only very indirectly linked. It's not in general possible to saturate a transformer core from the secondary. There is an exception to this for half wave rectification in small transformers with high resistance primary windings, and I have never seen this exception demonstrated.
Short and simple: For a given core, saturation determines the minimum number of primary turns for max. peak current to be expected.
Not exactly. Core saturation determines the number of turns and core area needed to withstand a certain amount of volt-time integral. That's not directly related to the peak output current to be expected. Primary magnetizing current is not the same as reflected secondary current. The two are only very indirectly linked. It's not in general possible to saturate a transformer core from the secondary. There is an exception to this for half wave rectification in small transformers with high resistance primary windings, and I have never seen this exception demonstrated.
As said, for a given core. Of course I meant max. peak value of magnetizing (not total) current. In a well coupled OT the (symmetrical) load current has no influence on saturation as primary and secondary load fluxes cancel. Magnetizing current is measured without load (open secondaries).