You guys probably already know this but......I set my Fluke 116 meter to "Auto-V Lo Z" and touch both ends of the capacitor. This way I can actually watch the voltage value drop to zero.
As you know low impedance mode uses something like 3k ohms to put a slight load on item measured in order to eliminate ghost (induced) voltages. Regular voltage mode is high impedance of around 10 Megohms which will take forever to drain capacitors.